Guest guest Posted December 26, 2008 Report Share Posted December 26, 2008 Dear Semco: One advantage that metal duct has over flex duct is that it interior is smooth sided, and so offers less resistance to air flow and consumes less energy for moving air through it. Many installations place a limit on the length of flex-duct that is allowed, probably due to this energy penalty. -- LIFE ENERGY ASSOCIATES 20 Darton Street Concord, MA 01742-5710 www.LifeEnergyAssoc.com -------------- Original message ---------------------- > Hello everyone. Again, can you PLEASE help me. > > I had an air conditioning contractor try to convince me that I should use metal > duct work > through out my house. The way he described it the metal had no insulation, but > was > wrapped with " bubble wrap " , then wrapped with foil. Yes, the same bubble wrap > used in > packing. > > My common sense is that this is only an invitation for moisture from the cold > metal and I > cannot imagine Bubble wrap being insulation for anything. Seems like it would > be an > invitation for MOLD. > > Other contractors are proposing using flex duct, which I understand has > fiberglass insulation > then coated with plastic in the center which will make a clean air compartment. > > Any thoughts, or remarks? All would be appreciated. > > Quote Link to comment Share on other sites More sharing options...
Guest guest Posted December 26, 2008 Report Share Posted December 26, 2008 Semco, etc. IMHO, metal (usually galvanized) ductwork is superior to flex. The flex wll cause greater disturbance of airflow within, thus reducing the efficiency of the system, and (something I recently learned myself (credit Tony Havics)) the coils used to keep the flex duct expanded actually create small eddies and dead spots in the airflow within the duct (part of the disturbance) resulting in greater accumulation of dirt within the duct. Flex duct can't be cleaned as easily or effectively as metal either due to the irregular interior surface, and the more fragile material. Therefore, I usually recommend replacement of the flex when it gets dirty. Not a big deal in easily accessible areas and short runs, so much depends upon your configuration. As I'm somewhat familiar with your situation and what you're striving to accomplish, I don't recommend using the flex. My familiarity with insulated metal duct is that it is usually insulated on the interior with fiberglass (NOT a good idea) or that the exterior is fiberglass wrapped. I'm not familiar with bubble wrap used as insulation, however it may pose some concers with the plastic offgassing. Otherwise, and theoretically, all insulation accomplishes it's purpose by creating dead air space. The concept of bubble wrap therefore makes sense from that perspective, as the bubbles, and once wrapped with foil, the entire bubblewrap structure becomes a series of symmetrical and contiguous dead air spaces. Not a bad idea, but I'd want more information including the type of plastic used & it's potential for offgassing, as well as R value ratings of the bubble wrap as compared to more traditional fiberglass outer wrapping. Fiberglass of course brings along it's own set of potential problems and concerns. I disagree that if the bubble wrap is properly engineered it's going to facilitate conditions favorable to microbial amplification. Like fiberglass, the plastic is non-organic and therefore does not supply a nutrient source. If there are no voids in the installation, or subsequent damage to the integrity of the bubble wrap insulation, there should be no condensation problems, as should be the case with any duct insulation. So again, it goes back to proper engineering, competent installation, and due care to ensure it is not damaged. I'd also want to know what the plastic material's expected useful lifespan is, and how it may be affected over time by heat and ozone exposure, which may cause more rapid deterioration. Bottom line is that if it were my house, I'd probably want metal duct with the exterior wrapped with fiberglass insulation, at least for the main lines, and particulary within wall cavities, etc., exept perhaps the inclusing of some short, accessible runs of flex duct to cut down somewhat on costs. Chuck Reaney Alpha Environmental, Inc. IAQ/IEQ & Environmental Consulting Media, PA 19063 P: F: C: Air Conditioning Duct Work Hello everyone. Again, can you PLEASE help me. I had an air conditioning contractor try to convince me that I should use metal duct work through out my house. The way he described it the metal had no insulation, but was wrapped with " bubble wrap " , then wrapped with foil. Yes, the same bubble wrap used in packing. My common sense is that this is only an invitation for moisture from the cold metal and I cannot imagine Bubble wrap being insulation for anything. Seems like it would be an invitation for MOLD. Other contractors are proposing using flex duct, which I understand has fiberglass insulation then coated with plastic in the center which will make a clean air compartment. Any thoughts, or remarks? All would be appreciated. Quote Link to comment Share on other sites More sharing options...
Guest guest Posted December 26, 2008 Report Share Posted December 26, 2008 Flexible duct has a high static pressure drop due to the ripple/concertina internal surfaces and therefore while you can use it for short runs, the agregate lenth of flexible duct should not exceed 6metres/20feet. This is why all long runs NEED to be mostly done in smooth solid duct. I also don't like the idea of the plasticised liners on a lot of ducts as the static generated by dust particles passing over the liner tends to conglomerate the dust into the valleys of the duct. Remember that the filters that you are probably using only entrain about 30% of the finer particles, that residue that still passes through your system either deposits within the system on the coils or the duct, or isw delivered into your conditioned space. The bubblewrap insulation may possibly be more of an example that the HVAC guy uses in his explanations than what is the reality. Anything with an R value better than 1.5 is probably ok for inside areas - but if the ductwork is exposed to outside air temperatures and humidity, you may wish to elevate this. We recommend that any flex duct on kitchen exhaust be replaced at not greater than 5-yearly intervals and the owners when they see the 5- year duct come out - usually want to replace with solid cleanable duct. So please don't think of flexible duct as being a healthy alternative. > > Hello everyone. Again, can you PLEASE help me. > > I had an air conditioning contractor try to convince me that I should use metal duct work > through out my house. The way he described it the metal had no insulation, but was > wrapped with " bubble wrap " , then wrapped with foil. Yes, the same bubble wrap used in > packing. > > My common sense is that this is only an invitation for moisture from the cold metal and I > cannot imagine Bubble wrap being insulation for anything. Seems like it would be an > invitation for MOLD. > > Other contractors are proposing using flex duct, which I understand has fiberglass insulation > then coated with plastic in the center which will make a clean air compartment. > > Any thoughts, or remarks? All would be appreciated. > Quote Link to comment Share on other sites More sharing options...
Guest guest Posted December 26, 2008 Report Share Posted December 26, 2008 Chuck, Thank you. Everything you said makes sense. I would agree immediately to medal ductwork that was wrapped in fiberglass insulation, just not the bubble wrap. The other concern I would have with metal would be 90 degree turns, which is not good. Fortunately, all the duct work will be run in the attic which will be conditioned. I will check further on the metal duct work using the fiberglass insulation on the outside of the ducts. Thanks again. > > Semco, etc. > > IMHO, metal (usually galvanized) ductwork is superior to flex. The flex wll > cause greater disturbance of airflow within, thus reducing the efficiency of > the system, and (something I recently learned myself (credit Tony Havics)) > the coils used to keep the flex duct expanded actually create small eddies > and dead spots in the airflow within the duct (part of the disturbance) > resulting in greater accumulation of dirt within the duct. > > Flex duct can't be cleaned as easily or effectively as metal either due to > the irregular interior surface, and the more fragile material. Therefore, I > usually recommend replacement of the flex when it gets dirty. Not a big > deal in easily accessible areas and short runs, so much depends upon your > configuration. As I'm somewhat familiar with your situation and what you're > striving to accomplish, I don't recommend using the flex. > > My familiarity with insulated metal duct is that it is usually insulated on > the interior with fiberglass (NOT a good idea) or that the exterior is > fiberglass wrapped. I'm not familiar with bubble wrap used as insulation, > however it may pose some concers with the plastic offgassing. > > Otherwise, and theoretically, all insulation accomplishes it's purpose by > creating dead air space. The concept of bubble wrap therefore makes sense > from that perspective, as the bubbles, and once wrapped with foil, the > entire bubblewrap structure becomes a series of symmetrical and contiguous > dead air spaces. Not a bad idea, but I'd want more information including > the type of plastic used & it's potential for offgassing, as well as R value > ratings of the bubble wrap as compared to more traditional fiberglass outer > wrapping. Fiberglass of course brings along it's own set of potential > problems and concerns. > > I disagree that if the bubble wrap is properly engineered it's going to > facilitate conditions favorable to microbial amplification. Like > fiberglass, the plastic is non-organic and therefore does not supply a > nutrient source. If there are no voids in the installation, or subsequent > damage to the integrity of the bubble wrap insulation, there should be no > condensation problems, as should be the case with any duct insulation. So > again, it goes back to proper engineering, competent installation, and due > care to ensure it is not damaged. I'd also want to know what the plastic > material's expected useful lifespan is, and how it may be affected over time > by heat and ozone exposure, which may cause more rapid deterioration. > > Bottom line is that if it were my house, I'd probably want metal duct with > the exterior wrapped with fiberglass insulation, at least for the main > lines, and particulary within wall cavities, etc., exept perhaps the > inclusing of some short, accessible runs of flex duct to cut down somewhat > on costs. > > Chuck Reaney > > Alpha Environmental, Inc. > IAQ/IEQ & Environmental Consulting > Media, PA 19063 > > P: F: C: > > Air Conditioning Duct Work > > > Hello everyone. Again, can you PLEASE help me. > > I had an air conditioning contractor try to convince me that I should use > metal duct work > through out my house. The way he described it the metal had no insulation, > but was > wrapped with " bubble wrap " , then wrapped with foil. Yes, the same bubble > wrap used in > packing. > > My common sense is that this is only an invitation for moisture from the > cold metal and I > cannot imagine Bubble wrap being insulation for anything. Seems like it > would be an > invitation for MOLD. > > Other contractors are proposing using flex duct, which I understand has > fiberglass insulation > then coated with plastic in the center which will make a clean air > compartment. > > Any thoughts, or remarks? All would be appreciated. > Quote Link to comment Share on other sites More sharing options...
Guest guest Posted December 27, 2008 Report Share Posted December 27, 2008 I would go with the sheet metal ductwork, also. Make sure it is properly sealed and insulated on the outside. Another potential benefit, is that the zinc in the galvanized metal is a natural anti-microbial, until the surface gets coated with dust, anyway. If the attic space is conditioned, some duct leakage may not be a critical issue. > > Hello everyone. Again, can you PLEASE help me. > > I had an air conditioning contractor try to convince me that I should use metal duct work > through out my house. The way he described it the metal had no insulation, but was > wrapped with " bubble wrap " , then wrapped with foil. Yes, the same bubble wrap used in > packing. > > My common sense is that this is only an invitation for moisture from the cold metal and I > cannot imagine Bubble wrap being insulation for anything. Seems like it would be an > invitation for MOLD. > > Other contractors are proposing using flex duct, which I understand has fiberglass insulation > then coated with plastic in the center which will make a clean air compartment. > > Any thoughts, or remarks? All would be appreciated. > Quote Link to comment Share on other sites More sharing options...